ISOCALC
5.0 USER MANUAL

INDEX
2.2 Anticondensation thickness
2.4 Temperature variations for tubes
2.5 Freezing time for tubes with static
fluid
3 Calculations relating to liquids not included
in the IsoCalc database
4 The use of IsoCalc for gas containing systems
7 How to interpret the results
9.1 Heat transfer between tubes
9.2 Heat transfer between flat surfaces
(sheets)
9.3 Heat transfer for convection and
radiation
IsoCalc 5.0 is a calculation program which
allows the scaling of materials for thermal insulation in order to obtain the
performance required by the end user e.g. heat loss, the prevention of
condensation, temperature drop, surface temperature and freezing times. It is
also possible to make energy saving calculation.
IsoCalc 5.0 is easy to use and therefore addressed
to everyone who works in the thermal insulation sector that has a basic
knowledge of the meaning of the data required by the program.
The end user should only have to insert the
correct data required, based on the system to be insulated, in order to obtain
the correct insulation thickness necessary and the desired performance. This
manual describes how to use the program, which data is required to make the
various calculations, how to insert them
and how to interpret the results.
Before using the results obtained to complete
the insulated system it is advisable to verify them first with our K-FLEX
Technical Department.
IsoCalc 5.0 bases its calculation on the
International Standard EN ISO 12241.
This version substitutes the previous one, 3.3,
and includes the following modifications:
-
Calculations
are based on EN ISO 12241 and no longer on VDI 2055
-
A
more “user friendly” lay-out permits you to reduce the windows dimension and to
always have access to the bar menu options
-
A
wider range of temperatures including cryogenic applications.
-
Now
available in other languages, (Italian, English, Spanish, German, Polish,
Russian, French).
-
Full
compatibility with Windows XP® , also without administrator privilege.
-
Internal
and external calculations for K-Flex cladding systems
-
Greater
information on “heat loss” and “freezing time” calculations.
-
Ability
to copy onto the clipboard for an easier spreadsheet use (e.g. Microsoft Excel®)
-
Update
of K-FLEX products and their
specifications.
-
A
wider database of fluids which help to calculate temperature variations without
having to actually recuperate the physical-chemical data
-
Energy
saving is expressed in €/KWh instead of lire/KWh
All in all, the flexibility of the program has
not been altered, and you can still use data as you please (like insulating
material specifications or the properties of fluids) to make comparative calculations,
to examine random cases, etc...
|
Fluids Type of calculation |
Liquid |
Gas* |
||||||
|
Tube |
Sheet |
Tanks§ |
Ducts# |
Tube |
Sheets |
Tanks§ |
Ducts# |
|
|
Heat loss |
√ |
√ |
√ |
√ |
√ |
√ |
√ |
√ |
|
Thermal
transmittance |
√ |
√ |
√ |
√ |
√ |
√ |
√ |
√ |
|
Energy
Saving |
√ |
√ |
√ |
√ |
√ |
√ |
√ |
√ |
|
Dew-point
Temperature |
√ |
√ |
√ |
√ |
√ |
√ |
√ |
√ |
|
Anticondensation
Thickness |
√ |
√ |
√ |
√ |
√ |
√ |
√ |
√ |
|
Safety
thickness limits |
√ |
√ |
√ |
√ |
√ |
√ |
√ |
√ |
|
Surface
temperature |
√ |
√ |
√ |
√ |
√ |
√ |
√ |
√ |
|
Temperature
changes for running fluids |
√ |
n.a. |
L |
$ |
√ |
n.a. |
L |
$ |
|
Freezing
time for static fluids |
√ |
n.a. |
$ |
$ |
n.a. |
n.a. |
n.a. |
n.a. |
|
Cooling
time for static fluids |
√ |
n.a. |
$ |
$ |
$ |
n.a. |
$ |
$ |
|
Temperature
changes for static
fluids |
$ |
n.a. |
$ |
$ |
$ |
n.a. |
$ |
$ |
n.a.: not
applicable
L The software does not allow this
type of calculation
* For
applications with Gas, see chapter 4
§ For tank
calculations, see chapter 5
# For duct calculations, see chapter 6
$
calculation can be made by referring to the indications in chapter.
By Heat loss we mean the amount of heat that
flows through an insulated system (tube, walls) in a specified time and is
expressed in W (= J/s). This amount has a sign which
indicates whether heat is actually lost from the fluid to insulate (minus sign)
or whether it receives heat (plus sign). The first situation arises when the
external temperature is lower than that of the fluid to insulate (liquid or
gas) and in the second, when the conditions are reversed. When the fluid is
heated, its temperature rises, whilst during heat loss the temperature drops.
This calculation is based on a static state,
and it refers to a stable condition between the fluid and the external
temperature. Therefore calculations made when a system is turned on or closed
down are not valid.
To find out how much heat is transferred (“heat
loss”), one needs the following data:
Ø
Temperature
of the fluid to insulate (see remark 1)
and the external temperature
Ø
Dimensions
of the duct to insulate: diameter (see remark
2) and the length of the tubes; surface and width for sheets
Ø
Thickness
and type of insulation
Ø
Surface
heat transfer coefficient “h”
It is useful to know which insulation thickness
can keep fluid heat loss below a desired amount, so by experimenting one can
calculate the necessary insulation thickness to guarantee an acceptable amount
of heat loss.
In situations where K-Flex insulation is not
used, the user can insert the lambda value of the chosen material, taking care
to use the value which refers to the mean working temperature of the insulation
(that means the average between the internal and external fluid temperatures; see remark 3). This is made possible by
choosing “K-factor” and inserting the correct value under the option
“Insulation material” (see fig.1).

Figure 1
The term “h” is the sum of the convective
surface heat transfer and for radiation of the insulation surface. This can be
inserted by the user or can be calculated by the software.
The software does not take into consideration
values of h>50, because normally they do not apply for typical insulations:
in the case of strong winds, it is more economical to install a windbreak
barrier, to also avoid erosion, instead of excessively increasing the
insulation thickness.
Calculation “h” for
tubes
The parameters to insert in order to calculate
“h” are:
Ø
Place
of insulation (external or internal)
Ø
Emission
coefficient “e” which is
intrinsic of the material, found on the external surface of the insulation (see remark 4). This determines radiation
heat transfer between the external surface of the tube and the environment.
Ø
For
calculations made in internal environments (fig. 2) the user will be asked how
the tube is placed (horizontal or vertical)

Figure 2
Ø
For
external installations (fig. 3), the user will be asked the following
information:
§
Wind
speed
§
Type
of covering (“cladding”, determines e; see remark 4)

Figure 3
Calculation “h” for
sheets
The calculation and the parameters required for
sheets are the same as those for tubes. However for sheets it is not necessary
to indicate whether they are placed horizontally or vertically, but the user
will need to indicate the height of the sheet (fig. 4), in order to make calculations
for internal and external installations.

Figure 4
For internal insulations the
software takes into consideration convective laminar air flows, and laminar or
turbulent flows for external insulations depending on wind speed.
Calculations regarding internal insulations
protected by a cladding are possible, by using the module for external
calculations and inserting “wind speed =
Apart from heat loss Q, the program also supplies you with the following data:
ü
The
average thermal conductivity lambda: the lambda value, intrinsic of the chosen
insulation material (eg.
ü
Thermal
transmittance K: is the heat transferred by degree and for surface unit (sheet)
or of the length (tubes) between the insulated system and the environment. It
is therefore the ratio between the heat transferred and the difference in
temperature between the fluid and the environment, expressed in [W/m2K]
for sheets and in [W/mK] for tubes
ü
Energy
saving: this is the percentage of heat that is not lost thanks to the
insulation, compared to the same system without insulation.
This calculation is used for cooling systems,
or for those where the fluid temperature is lower than that of the environment.
In this case it is important to know the minimum thickness of the insulation that
ensures a sufficiently high surface temperature to avoid the formation of
condensation of water vapour on the insulation (see remark 5).
In order to make this calculation the following
data is required:
Ø
Both
fluid (see remark 1) and external temperature (see remark 6)
Ø
Relative
humidity of the environment (see remark 6)
Ø
Dimensions
of the duct to insulate: diameters for tubes (see remark 2); height for sheets
Ø
Type
of insulation
Ø
Surface
heat transfer coefficient “h”
The result of the calculation is:
ü
The
temperature of the formation of condensation relating to the inserted degree of
humidity and ambient temperature
ü
The
theoretic minimum thickness to prevent the formation of condensation
ü
The
dimensions of the K-Flex insulation suitable for the situation, the thickness
of which is the next one greater than the
theoretic one.
This function allows the user to calculate what
the temperature will be on the external surface of an insulation material,
applied with a given thickness on a duct. In reality the surface temperature is
calculated by all the IsoCalc calculation modules, but the user is only able to
discover it with this function. To make this calculation, the following is
needed:
Ø
Temperature
of the fluid to insulate (see remark 1) and that of the external environment
Ø
Dimensions
of the duct to insulate: diameters for tubes (see remark 2); height for sheets
Ø
Type
and thickness of the insulation
Ø
Surface
heat transfer coefficient “h”
However efficiently a fluid may be thermally
insulated, the heat transfer with the outside will never be completely stopped. This means that the
temperature of the fluid to insulate will differ along the duct in which it
flows according to the heat transferred and to the intrinsic characteristics of
the fluid. The calculation “variations in temperature” allows the user to
discover the variation in temperature of the fluid after having passed through
an insulated pipe at a given speed. To make this calculation the following is
needed:
Ø
Both
the temperature of the fluid on entry into the pipe (see remark 1) and that of the external environment.
Ø
The
dimensions of the pipe to insulate: diameter (see remark 2) and length
Ø
The
specific heat and the density of the fluid (the default data refer to water).
Ø
The
flow speed of the fluid
Ø
Type
and thickness of the insulation
Ø
Surface
heat transfer coefficient “h”
The result is:
ü
the
temperature variation of the internal fluid after having passed through a given
length of tube.
ü
Heat
loss Q re-calculated to the mean temperature of the fluid, that is to say Tm =
(Tentry-Texit)/2
In the case of static fluid in a cold
environment, over a certain period of time the loss of heat from the fluid will
lower the temperature. If the environmental temperature is lower than the
freezing point of the fluid in question, (eg.
The time required for the freezing process depends
on the efficiency of the insulation: the more the fluid is insulated, the
slower will be the heat and temperature. The program allows you to calculate
freezing time as function of:
Ø
Both
the initial temperature of the fluid (see
remark 1) and the ambient temperature
Ø
The
dimensions of the pipe to insulate
Ø
Specific
heat, latent melting heat and freezing temperature of the fluid (the default
data refer to water)
Ø
The
formation of ice (the percentage of the mass of water that will solidify)
Ø
The
type and thickness of insulation
Ø
Surface
heat transfer coefficient “h””
If the user only needs to know the time to
reach freezing temperature, the value “0%” should be inserted in the “formation
of ice” field (see remark 7).
With the module “freezing time” it is also
possible to calculate the cooling time required for a liquid to arrive at a
final required temperature. It is necessary to modify the following fields, by
inserting the following data (see note 8):
Ø
Freezing
temperature = final temperature
Ø
Formation
of ice = 0 %
To calculate the variation in temperature and
the liquid freezing time, the program makes the data of the following liquids
available: water, milk, beer, ammonia, heavy and light crude, ethylene glycol
and glycerin. Should it be necessary to make
calculations based on liquids not included in this list, the operations are
possible if the user already knows the physical-chemical data relevant to the
liquid in question, inserting them in the requested fields (overwriting the
default values):
-
density: this is the ratio between the weight and the
volume occupied by the liquid. This is dependent on the temperature, therefore
to make precise calculations it is advisable to use the data which refers to
the internal temperature. IsoCalc requires the following units of measure:
[Kg/m3] = 1000 [g/ml] = 1000 [Kg/l]
-
freezing temperature: this is the solid<>liquid
transition temperature, i.e. at which a liquid solidifies or a solid melts.
IsoCalc requires the data as [°C], therefore the eventual conversion from
Kelvin degrees [K] is: °C = K-273
-
specific heat: indicated as Cp, this describes how much heat is necessary to increase the fluid
temperature by
-
latent melting heat: indicated as DHfus, this is the heat
required to melt a solid (or the heat to be extracted from a liquid to solidify
it). This is expressed as [J/g], numerically the same as [KJ/Kg] which is the
format required by IsoCalc.
An interesting database for this data can be
found for example at www.engineeringtoolbox.com
The IsoCalc calculation formulas
which are valid for liquids give results which are in some cases also valid
(approximately) for gas containing systems.
An important value which helps the
user to verify whether results are reliable in the case of tubes or ducts is
the speed of gas: the higher it is (very turbulent), the more its behaviour
resembles that of a liquid. Therefore the higher the speed of the gas, the more
negligible is the difference between the IsoCalc result and that calculated for
gases.
Moreover, the results supplied by
IsoCalc are always conservative, both in the case of tubes, ducts and tanks,
which means that heat losses and temperature differences are overestimated, so
calculated insulation thicknesses in reality will give higher performances, as
can shown in the table below:
|
Case |
IsoCalc results (referring to a liquid) |
Suitability for systems containing gas (conservative approximation) |
|
Tambient > Tinternal |
1) Heat loss 2) T-surface (for anticondensation
thickness) 3) variation T |
1) yes, since Qliq > Qgas,
losses will be slightly overestimated 2) yes: since Tliq < Tgas
the thickness will be slightly oversized 3) the software calculates variations
of T always greater that actual ones |
|
Tinternal > Tambient |
1) Heat loss 2) T-surface (for safety limits) 3) variation T |
1) yes, since Qliq > Qgas 2) yes: since Tliq > Tgas
the scaling for safety limits is based on a worse situation 3) the software calculates variations
of T always greater that actual ones |
We advise you to consult the K-FLEX
technical support when interpreting results.
IsoCalc 5 is not equipped with a calculation
formula for tanks. However it is possible to make certain calculations by carefully comparing the tank to a cylindrical tube
or a sheet, depending on the cases, as described below.
In the case of tanks there is not a stable condition since the temperature of the fluid
held within changes continuously, becoming closer to that of the environment; the
time depends on the type of fluid, the dimensions of the tank, the
characteristics of the insulation and environmental conditions. Results
obtained with IsoCalc, which we repeat are based on a stable condition, are
therefore approximate because they take into account the initial fluid
temperature.
However this approximation represents a
conservative situation and is therefore extremely valid for practical purposes
(see also chapter 7). In any case, an indepth examination of tanks, which also
takes into consideration the internal heating and agitating systems, is beyond
the capacity of this software.
If a fluid is contained in a rectangular tank,
it is possible to make the following calculations:
-
Heat
loss
-
Surface
temperature
-
Anticondensation thickness
by using the module relating to sheets.
To calculate heat loss, it is necessary to
calculate the average heat transfer area by using the following formula

A = (2a + 2b + 4s)L +
2(a+s)(b+s); s = insulation thickness
If the tank is cylindrical, it is possible to
use the module relating to tubes to make the following calculations:
-
Heat
loss
-
Surface
temperature
-
Anticondensation
thickness
To calculate heat loss, it is necessary to
treat the tank as a tube of the same length, in such a way that the 2 transfer
surfaces represented by the bases of the tank are included in the calculation.
The equivalent length of such a tube represents the height of the tank increased by a sufficient amount so that the total heat transfer area obtained is
roughly equal to the real one of the tank.
To calculate the equivalent length one can use
the following formula:

where s = insulation thickness; D (diameter of
the insulated tank) = d + 2s
Using this equivalent length Leq it
is possible to apply the heat loss results with an acceptable approximation
(error << 1%). The other results are more or less precise because they do
not depend on the total transfer surface.
In order to make calculations for rectangular
ducts, one must use the module for the calculations of sheets, after having
calculated the average heat transfer area of the duct using the following
formula:

A = (2a + 2b + 4s)L; s
= insulation thickness
§
Approximations used
All calculations are based on the
temperature of the liquid at the source of the system to be insulated.
However this temperature is not
constant (for example see the “variation in temperature” module) because the
longer the distribution system the closer this will resemble the environment
temperature. This means that the difference between the internal and external
temperatures is reduced along the distribution system: making the calculation
at the source of the system, where the difference in temperature is greater,
will therefore represent a conservative approach, important for the scaling based on heat loss, energy saving and hourly
costs.
§
Heat loss Q
The quantity Q expressed in [W] (J/s) describes the heat lost from the system
every second: lost (minus sign) or gained (plus sign). The exact definition of Q is “loss of power” since Q has the same unit of measure as power.
By multiplying Q by a chosen length
of time (expressed in seconds) one can calculate the amount of heat that is dispersed
in [J], or how much energy (heat = energy!) is wasted by the system in that length
of time (e.g. 1 month, 1 year, etc...). Usually kilowatthour [KWh] is used to
measure energy which is the product of Q
(expressed in KW) for time expressed in hours, since the price of energy refers
to KWh.
→ Example: if the result of the
calculation is Q = 12.124 W and one
wants to know the amount of energy dispersed in one year, then:
-
1
year = 365x24 = 8760 hours. Q = 0.012124 KW => energy dispersed =
106.2 KWh
§
Energy saving / alternative
Every KWh which does not reach its
destination, because it is dispersed along the duct, represents a loss in terms
of cost. We could use as an example a pipe which carries hot water from a water
heater to a shower. Thanks to the insulation one can reduce the amount of heat
that is dispersed and therefore save money (for example by lowering the
temperature of the boiler). IsoCalc 5 depicts this quantity as the percent of
heat that can be saved compared to the same system without any form of
insulation: ![]()
→ Example: Tube diameter = 25mm, Tint
=
Using K-Flex ST
In the field below the “hourly cost”
field the user can choose the thickness of a K-Flex product and see approximately
what the heat savings would be (in order to obtain a more precise value the
user must repeat the calculation inserting this thickness in the “insulation
thickness” field; see remark 9)
§
Hourly cost
The hourly cost calculates the heat
dispersed every hour as “lost money” per hour, multiplying the heat loss Q
(expressed by KW) by the energy cost: the latter being indicated by the user in
the correct field as cost per KWh (default
value = 0.500 €/KWh)
→ Example: Q = 620 W => hourly cost
= 0.31 €
§
Temperature for the formation of
condensation / anticondensation minimum thickness
Condensation forms on piping with
lower temperatures than those of the environment if the humidity in the air is
sufficiently high. For all ambient temperatures (Tamb) and their
relative humidity (
The temperature of condensation
formation completely depends on the ambient temperature and its
The calculation “surface
temperature” is used to calculate the minimum insulation thickness so that the surface
temperature of the insulated tube is greater than that of condensation
temperature.
However, in the field “dimensions of K-Flex insulation”, IsoCalc
suggests the K-Flex product which has a minimum thickness range greater than
that of the anticondensation range.
→ Example: anticondensation thickness
= 14.6mm (with a
§
Surface temperature
Knowing the insulation surface
temperature allows one to evaluate the suitability of the insulation for its
chosen application: apart from heat saving it may be necessary to know whether
it is compatible with other structures in the immediate vicinity, or whether
being close to the insulation could cause any risks (safety limits). The
possibility of the formation of condensation is a topic that has already been
discussed. By increasing the thickness of the insulating layer, the surface
temperature becomes closer to that of the environment.
§
Temperature variations
The variation in temperature (that
is usually indicated as DT) allows the user to know the final temperature of the liquid when it
exits the pipe.
The result of the temperature
variation DT is subtracted
from the temperature of the liquid on entering to arrive at the exit
temperature.
→ Example: if with Tinitial
=
Therefore the user can decide
whether this final temperature is still within the limits imposed by the
project or whether it could create problems for the liquid (e.g. it may reach
boiling or freezing temperature).
§
Freezing time / alternatives
Freezing time tfreeze,
indicated in hours, is the time required for the change in temperature of the
liquid from its initial temperature to its freezing temperature. Moreover, if
in the “formation of ice” field the user inserts a value grater than 0 %, for
example 20%, the resulting time includes also the time for solidifying 20% of
the liquid present.
→ Example: formation of ice = 0% => tfreeze = 0.23 h (= 13’48”)
formation
of ice = 20% => tfreeze = 4.04 h (= 4h2’24”)
IsoCalc also shows the freezing time
which relates to the K-FLEX products’ available thicknesses.
Please not: for calculations based
on the two types of crude oil (light and heavy) included in the software, as
the freezing temperature the “pour point” is considered, that is the
temperature at which the liquid becomes so thick to make it difficult to flow
through a pipe. This temperature however does not correspond to a phase-change,
therefore the Cp value is used as the “latent heat” to calculate the time
necessary for the formation of a given percentage of solid (or better: of
viscose oil).
1)
IsoCalc 5.0 fixes the maximum
temperature limit of liquid to insulate at
2)
The diameter to use as a reference
when inserting the correct value of the insulation is the external diameter
of the tube, that is the internal diameter of the tube (through which the
liquid flows) increased of the double of the pipe-wall thickness..
3)
The exact average working
temperature is the average between the surface
temperature of the tube (≈ internal fluid temperature) and that of the
external surface of the insulation: for a precise calculation an additional
operation is required. Using an approximate value as that of the software (as regulations prescribe), the calculated heat loss
is greater than the real amount if Text >Tint
(conservative example), and less than the actual amount if Text
<Tint (also a conservative example for “cold” applications).
4)
The default value e = 0.93 refers to the uncovered black elastomeric foam, as K-Flex ST.
Using a K-Flex product of a different colour (for example K-Flex ECO, green)
the e value should be modified => see remark 9.3
5)
The“anti condensation”
calculation is a part of the “surface temperature” calculation, in as much as
the surface temperature is calculated based on the insulation thickness until
it is the same as the vapour condensation temperature
6)
To make a reliable anticondensation
thickness calculation, one must first find out the true environmental
conditions to which the insulation is subjected, or to which average
temperature and humidity the insulation is placed during its working period .
These values are chosen with common sense, in a conservative manner, therefore
it is important to examine the following examples:
-
if the relative humidity (
-
if the temperature value and UR
change during the working period, to make the calculation one can use the worst
situation (maximum humidity and the corresponding temperature or the minimum
temperature and the corresponding humidity), or the average conditions, after
having calculated how long these extreme conditions persist and how sensitive
the system is when tested for the formation of condensation.
-
if the user does not have the
temperature and
It is important to note that, especially for external installations, it
would be logical to use conditions that allow one to preserve the installation
from condensation for a reasonable
length of time (for example, 90% of the working time), in order to avoid
excessively re-scaling the insulation. In the space of one day there could be
high oscillations of temperature and humidity, and usually, the lowest
temperature corresponds to the lowest amount of humidity. There are also
moments during the day (for example at dawn) when the atmospheric humidity
reaches its saturation point, which changes rapidly, as one can see by noticing
the formation of dew on a field and its later disappearing.
The software accepts a maximum humidity value of 96%. Over this value,
in fact, insulation thicknesses increase excessively, so it would be only
logical to increase ventilation in the rooms, change the coefficient of
emission or change other parameters. This is applicable for rooms such as
kitchens, bathrooms, shower rooms etc, where an anticondensation thickness
calculated based on average humidity would be inefficient.
It is advisable to consult the K-Flex technical division when problems
occur
7)
To make the calculation of the freezing
time, pay attention to the value inserted in the “formation of ice”
field. In fact, this field allows one to calculate the time necessary to obtain
a partial or a total solidification of the liquid, indicated as a
percentage of the mass of liquid in the “formation of ice” field. This value
could prove useful if the user needs to know, for example, how much time passes
before the piping becomes blocked (partially, 0-99% “formation of ice”, or
totally, 100% “formation of ice”) caused by solidification of the liquid. In
many practical situations, the formation of ice of up to 25% of the total
surface is considered acceptable.
8)
To make the calculation of cooling
time the user should take into account the following examples, where it is necessary
to calculate the time that it takes for a liquid to pass from
→ Example: the various fields should be filled in as follows:
-
Ambient temperature =
-
Internal temperature =
-
Freezing temperature =
-
Formation of ice = 0%
If the liquid in question is not included in IsoCalc, it will be
necessary to also fill in the fields relative to density and specific heat (see
chapter 3), while the field relative to latent heat is not necessary for this
calculation.
9)
The approximation of energy saving obtained by choosing one of the thicknesses in the “alternately
calculated for K-Flex dimensions” field, is a result
of the fact that heat loss is recalculated substituting only the new
chosen thickness, without recalculating “h”.
Heat Q
[W] transferred through an insulated tube is:

Ti, Te = internal and external temperature of
the tube, respectively [°C o K]
L = length of tube
d = internal diameter of tube [m]
D = external diameter of the insulated tube [m]
a = coefficient of heat transfer for convection
(fluid -> internal tube) [W/m2.K]
h =
coefficient of superficial heat transfer (convection and radiation between the
insulated surface and the environment) [W/m2.K]
l = Thermal conductivity of the insulation [W/m.K]
Heat Q
[W] transferred through an insulated sheet is:

A = sheet surface [m2]
s = insulation thickness [m]
a = coefficient of heat transfer for convection
(fluid -> internal wall) [W/m2.K]
h = coefficient of superficial heat transfer
(convection and radiation between the insulated surface and the environment)
[W/m2.K]
l = Thermal conductivity of the insulation
[W/m.K]
Usually a is ignored in the calculation of Q, since heat transfer convection of a
flowing liquid is so efficient that the term 1/a is almost zero.
The term h
is the sum of the heat transferred for convection and for radiation of the
external surface of the tube or sheet and the environment:
h = aconv + airr
aconv depends on the: surface temperature (Tsup),
the dimensions of the insulated tube/sheet, the speed of the external air, the
position of the tube/sheet. The calculations are based on semi-empirical
formulas. The exact formulas are described in EN ISO 12241.
airr, the term referring to radiation, is only
dependant on the difference in temperature between the external surface of the
insulation (Tsup) and that of
the environment:
airr = e.e0
e0 = coefficient emissivity of black colour =
5.67 10-8 [W/m2K4]
e = coefficient emissivity of the surface
material (insulation, coverings ...)
The coefficient e depends on the color of the material: as a
general rule, the darker it is, the higher the e value is. One must bare in mind that material
subjected to radiation, the one that e refers to, is the one on the outermost surface of the insulation;
usually the covering of the insulation, the insulation itself without any
covering, or the material of the tube (iron, steel, copper, etc.) for
calculations without insulation.
IsoCalc 5.0 lists the e for the
For grey (eg. K-Flex H) or green coloured
products (eg. K-Flex ECO) the e value is
approximately 0.80
However the e values are tabulated in
literature for every type of material (see for example VDI 2055 or www.engineeringtoolbox.com)
The exit temperature of a running fluid in a
tube (Tf) is given with the
following formula:

Te = external temperature [°C o K]
Ti = temperature of fluid on
entering [°C o K]
k = heat transmittance [W/m.K] => see
chapter 2.1
L = tube length [m]
Cp = specific fluid heat [J/Kg.K]
d = flow rate [Kg/s]
If the fluid is resting, the following is used:

Te = external temperature [°C o K]
Ti = fluid temperature on entry [°C
o K]
k = heat transmittance [W/m.K] => see
chapter 2.1
t = time [s]
Cp = specific fluid heat [J/Kg.K]
m = mass of fluid [Kg]
Freezing time is the sum of the time necessary
to bring the liquid to its freezing temperature (or fusion) plus the time
needed to solidify the percentage of the liquid indicated by the user. The
formula for the temperature variation time and the equation which gives one the
amount of heat to subtract from a mass of liquid m to render it solid DHfus .m = Q, are used respectively.
The freezing time, in hours [h], is given by:

Te = external temperature [°C o K]
Ti = initial temperature of the
fluid [°C o K]
Tcong = freezing temperature (or
fusion) [°C o K]
k = heat transmittance (see chapter 2.1) for
heat transfer from Ti to Tcong [W/m.K]
L = tube length [m]
m = liquid mass [Kg]
x = percentage of solid formation compared to
the initial mass
DHfus = melting latent heat (or
solidification, see charter 3) [KJ/Kg]
Cp = specific fluid heat [KJ/Kg.K]
Q = heat transferred to the environment of the
liquid at freezing temperature [W]
THIS SOFTWARE IS PROVIDED 'AS IS'
WITHOUT WARRANTY OF ANY KIND. THE ENTIRE RISK AS TO THE RESULTS AND THE
PERFORMANCE OF THE SOFTWARE IS ASSUMED BY THE USER, AND IN NO EVENT WILL L’ISOLANTE
K-FLEX S.R.L BE LIABLE FOR ANY CONSEQUENTIAL, INCIDENTAL OR DIRECT DAMAGES
SUFFERED IN THE COURSE OF USING THE SOFTWARE.
THE CALCULATIONS ARE PROVIDED
"AS IS", WITH NO WARRANTIES WHATSOEVER. ALL EXPRESS, IMPLIED AND
STATUTORY WARRANTIES.
LIMITATION OF
LIABILITY:
UNDER NO CIRCUMSTANCES SHALL L’ISOLANTE K-FLEX S.R.L BE LIABLE TO ANY USER ON
ACCOUNT OF THAT USER'S USE OF THE SERVICES. SUCH LIMITATION OF LIABILITY SHALL
APPLY TO PREVENT RECOVERY OF DIRECT, INDIRECT, INCIDENTAL, CONSEQUENTIAL,
SPECIAL AND EXEMPLARY DAMAGES (EVEN IF L’ISOLANTE K-FLEX S.R.L HAS BEEN ADVISED
OF THE POSSIBILITY OF SUCH DAMAGES), ARISING FROM ANY USE OF THE SERVICES
(INCLUDING SUCH DAMAGES INCURRED BY THIRD PARTIES).